I have made a model of 40 storys and run smoothly if set all the pile supports as pinned. However, after I changed the supports to bi-linear, it said that the model is non convergence and stop running. Attached is my file and please advise on how to fix it. Thanks a lot
The file is here
https://drive.google.com/file/d/0B9ols5HBjkCca2x4N2FmWG9ZaVU/edit?usp=sharing
I am not very familiar with ROBOT analysis. I tried the same model with 36 floors but changed to pinned supports. The model can run without warnings of non-convergence. Please advise what I should do to re-construct / improve the model? Thanks a lot.
https://drive.google.com/file/d/0B9ols5HBjkCcdnQ0blEzUG1sakU/edit?usp=sharing
Some remarks:
- mesh model properly - for example mesh size 1m, no regular mesh, no kinematic links - many posts about that on this forum
- check your model - see example screen capture below
claddings created on top of panels (exmple 8857) will not transfer loads to panels \ FEs
I hope panels like 8858 8859 are intentionally set as Curtain Wall by you