I'm calculating a tank and I have tried to let Robot calculate the minimum reinforcement for me but it seems to me that the values are to high.
I have the reinforcement type with simple bending.
The pictures in the pdf show part of the bottom of the tank and its 700 mm of concrete C40/50 (fctm=3.5MPa) at most and the minimum reinforcement is 17.6 cm2/m.
If I use the formula AsMin = 0.26 * (fctm / fyk) * b * d I get app 12 cm2/m. (fi16 fyk=500MPa)
What is the explanation to this difference?
If I change the type to "bending+compression/tension" to concider normal forces in the slab I get over 80 cm2/m in minimum reinforcement in some areas.
Do you have any explanation to this?
Please check the code provisions for max. allowed bar spacing.
http://forums.autodesk.com/t5/Robot-Structural-Analysis/Minimum-reinforcement-on-slabs/m-p/3729178
The minimal area of reinforcement for tension is usually defined by different formula tan the value for bending.
Yes the maximum distance is 250 mm according to 9.3.1.1 (3) which is 4*2,01=8,04 cm2/m.
Try to set the steel grades and bar sizes in the reinforcement parameters labels assigned to panels.
I did that in my model from the beginning. It must have lost that setting in some way.
The difference is that when I choose B500BT as reinforcement grade it says "plain" instead of "deformed". Maybe that's the problem?
When I choose B500BT in the "Plate and shell reinforcement type" it says "Plain" but according to the database it should be deformed.
Please check if you have a local version of this database in C:\Users\username\AppData\Roaming\Autodesk\Structural\Common Data\Robot version number and delete or move it.
I moved it and now it is "deformed" both in the "type"-dialog and in the database.
I have investigated the result a little bit more and I find that the result of the minimum reinforcement is depending on if you check the "Reinforcement adjust" for cracking in the SLS tab of the "Plate and shell reinforcement type".
I can't find a description of that tab in the Robot-help.
If that setting is unchecked I get results that correspond with 9.2 and 9.3 in EC 1992-1-1.
But if I check it I get much more minimum reinforcement even if there are no cracks. I wonder if the program uses 7.3.2 in EC instead and calculates the effective area of the concrete tension zone regarding the stress distribution?
Or if not how is it done?
So you were using your local (edited) version of the database. Mystery solved
Formula (7.1) from 7.3.2
