Accepted Solution

Load Combination Regulations EC7

399 Views, 6 Replies
01-06-2012 11:04 PM

In ULS verification under EC7, partial factors for variable actions may be taken as 1.5 if unfavorable and 0 if unfavorable.  Does the regulation file consider this? I notice only the value of γ-max (=1.5) is defined whilst the field for γ-min is blank.  Please see attached

Please use plain text.
Product Support
Artur.Kosakowski
Posts: 5,111
Registered: ‎12-17-2010

Re: Load Combination Regulations EC7

01-09-2012 12:37 AM in reply to: stroxy

When the code combinations are generated they include ones that include only deal loads (live and snow loads with 0 load factors) dead loads and live loads (snow loads with 0 factors) and dead loads with selected live loads (other live loads with 0 load factors) therefore there is no need to put 0s as the load factors in the regulation file.

 

If you find your post answered press the Accept as Solution button please. This will help other users to find solutions much faster. Thank you.

 

 



Artur Kosakowski
Please use plain text.
Mentor
stroxy
Posts: 190
Registered: ‎12-06-2011

Re: Load Combination Regulations EC7

01-09-2012 10:47 AM in reply to: Artur.Kosakowski

 

Thanks Artur, what about the scenario where different limit states recommend different values for γg, as in the attached tables.  How does one incorporate this in the regulations?

Please use plain text.
Product Support
Artur.Kosakowski
Posts: 5,111
Registered: ‎12-17-2010

Re: Load Combination Regulations EC7

01-10-2012 02:26 AM in reply to: stroxy

The A type with 0.9 for dead loads is used in the PN regulation whereas additional reduction of dead loads due to existence of live loads is used in the Belgium version of Eurocode.

 

If you find your post answered press the Accept as Solution button please. This will help other users to find solutions much faster. Thank you.

 

 



Artur Kosakowski
Please use plain text.
Mentor
stroxy
Posts: 190
Registered: ‎12-06-2011

Re: Load Combination Regulations EC7

01-10-2012 03:34 AM in reply to: Artur.Kosakowski

So if I understand you correctly, that means to check the 2 limit states EQU and STR for example, I will have to run 2 different analysis with the corresponding regulations for each limit state

Please use plain text.
Product Support
Artur.Kosakowski
Posts: 5,111
Registered: ‎12-17-2010

Re: Load Combination Regulations EC7

01-10-2012 04:05 AM in reply to: stroxy

One analysis with two sets of combinations generated with different regulation files. The steps are shown on the attached picture.

 

If you find your post answered press the Accept as Solution button please. This will help other users to find solutions much faster. Thank you. 



Artur Kosakowski
Please use plain text.
Mentor
stroxy
Posts: 190
Registered: ‎12-06-2011

Re: Load Combination Regulations EC7

01-10-2012 04:46 AM in reply to: Artur.Kosakowski

Many thanks Artur!! 