Hollow slabs self weight
Stilie87
Stilie87
I discovered that by using hollow slabs in Robot the self weight is not calculated correctly. I Would like to use Hollow slabs to get the right load-distrubution and the correct shear/bending stiffnesses.
Moments should be around 140 kNm ant not ~60 as shown in the file.
What is wrong?
Is the Hollow-slabs parameters not correct.
Rafal.Gaweda
Autodesk Support
Autodesk Support
My = robot calculations according your thickness data
Rafal Gaweda
Stilie87
So you can not use Hollow slabs if you want to calculate the correct moments?
Rafal.Gaweda
Autodesk Support
Autodesk Support
It is correctly calculated according to data you entered to robot. This data is not coherent to your drawing dimensions so...
Examples:
hole - circular vs elipsoid
distance between holes centers 224 vs 150
thickness of plate 265 vs 500
etc
Rafal Gaweda
Stilie87
OK
So what is the correct parameters to put into the hollow slab to get the correct stiffnesses and the correct self weight ( 6,6 kn/m¨2) ??
Artur.Kosakowski
Autodesk Support
Autodesk Support
or exclude this panel from self-weight  load list and replace it with the 6.6 uniform load on the panel.
If you find your post answered press the Accept as Solution button please. This will help other users to find solutions much faster. Thank you.
Artur Kosakowski
saclovitzky
Hello Artur,
Is this the right way to obtain/input the specified unit weight of Hollow core slab?
I'm just wondering , why you are using "unidirectional ribs" instead of hollow core slab?