DESIGN - RC Columns Safety Factors

Dear Colleagues

 

Could I know why does the moment safety factor for the calculated column equals zero since any concrete section has capacity and there is applied loads ?

 

Kindly ,  take a look to the attached model and capture .

 

Note 01 : this case was occurred in elements  (4787,4788,4793 and 4794).

Note 02 : if you use any capture for explanation . Please send it as attached

 

http://www.2shared.com/file/O5PAcQiG/Columns_Safety_Factors.html

 

Thanks in advance

Refaat

2 REPLIES 2
Message 2 of 3
Artur.Kosakowski
in reply to: Refaat

The 'basic' value of capacity calculated by Robot is Rd/Sd value and this one should be used as the primary reference..

The other two are sort of informative: what would be the bending capacity for given level of axial force and vice versa. In case of the compression forces being above the critical one there is no 'additional' bending capacity in the column.

 

If you find your post answered press the Accept as Solution button please. This will help other users to find solutions much faster. Thank you.

 

 

 



Artur Kosakowski
Message 3 of 3
Refaat
in reply to: Artur.Kosakowski

Dear Artur

 

Clear , thanks for your perfect response

 

Refaat