Robot Structural Analysis Forum
Welcome to Autodesk’s Robot Structural Analysis Forums. Share your knowledge, ask questions, and explore popular Robot Structural Analysis topics.
Design of thin walled C section
9 REPLIES 9
Message 1 of 10
945 Views, 9 Replies
Hello all
I have made 2 different thin walled sections of the same geometry but different gauges in robot. I have gone through the procedure of calculating all the section properties and then adding the section to the thin walled database and manually adding all the section proerties to it.
I have then created the design paramters and checked thin walled section design.
The strange thing now is when the two sections are used the thicker section of the two comes out as a higher utlistation. (I have used one section with 2mm and one with 2.5mm thickness).
Looking into the calculations it seems that for the thinner section it does not calculate the effect elastic modulus (Weff,y; Weff,z) but does so for the thicker section which therefore leads to reduced section properties below that of the 2mm thickness.
Would there be a reason for this in the programs calculations? I cant undertand why there would be no calculation for reduced section properties of the thinner 2mm section. They are both set to the same deisgn parameters, experience the same forces and the section properties for both sections are correct.
Thank you for your time.
Oscar
9 REPLIES 9
Message 2 of 10
Artur.Kosakowski
Message 3 of 10
in reply to: Artur.Kosakowski
Hi Arthur
Yes I have followed what was done in the first link. I have done this quite alot and haven't come across this before.
Thanks for the quick reply!
Oscar
Message 4 of 10
Artur.Kosakowski
Could you attach the both rtd file and your user section database and indicate on a screen capture what to look at please?
Artur Kosakowski
Message 5 of 10
attached is the model file
Message 6 of 10
attached below is the section databse
Message 7 of 10
below are the images attached
Sorry for doing this in 3 seperate posts I have only just realised you can add more than one attachmemnt!
Thanks again
Message 8 of 10
Artur.Kosakowski
The 2.5 mm section has got the ends of C shape defined as 11 mm straight parts. Robot during the thin wall section verification checks its geometrical 'correctness' too. In case of such short reinforcement of the flange the c/b ratio is calculated to determine if it has got sufficient stiffness to be recognized as such. The check is done according to the paragraph (5.2.(2) of EN 1993-1-3 (formula 5.2a):
For the above mentioned section c/b = 11/65 = 0.169 < 0.2 therefore this vertical part is not considered as the reinforcement for the flange of the C shape meaning the flange is of class 4 becoming a cantilever rather than being supported at both ends.
Artur Kosakowski
Message 9 of 10
Thank you Artur! You are a genius I would have never found that!
Message 10 of 10
ga137
Is it possible to add a Double Channel section by the second method mentioned, as a thin member, and then perform cold formed steel design? I am having issues in the cold form design of some complex shapes such as double sigma section etc.