When doing a column base design in the connections module, most of the time the connection fales due to concrete cone pullout or an other form of concrete failure and not due to failure in the steel parts.
These concrete failures can be prevented by using reinforcement bars in the concrete. However it is not possible to enter this reinforcement in the design module.
How can I calculate such a connection within Robot incorporating both steel and concrete details?
Solved! Go to Solution.
Solved by Artur.Kosakowski. Go to Solution.
As you wrote such anchorage type is currently not available in Robot therefore the check has to be done in some other way. E.g. ignore the corresponding verification part done by Robot and replace it by hand calculations or in Excel based on forces imported from Robot.
If you find your post answered press the Accept as Solution button please. This will help other users to find solutions much faster. Thank you.
Definitely the next release is not possible (already too late ). Are you able to point me to some good references where I can find the description of this kind of anchorage verification procedure? Thank you.
I have a reference, but it is in Dutch and not available in English. It is:
CUR / BmS-rapport 10: Kolomvoetplaatverbindingen
written by D.A. Hordijk and J.W.B. Stark
ISBN 978-90-72830-82-1
Hi,
It is a very useful idea for all users if we could choose not to have the concrete checks (CEB design) by means of a simple option in the connection interface.
In this context also, it would be great if more anchor types could be added (like Peikko PPM & HPM) or a general anchor type with user tension & shear capacities and NO concrete checks.
Marios.
MARIOSZISSIMATOS5169 wrote:
Hi,
It is a very useful idea for all users if we could choose not to have the concrete checks (CEB design) by means of a simple option in the connection interface.
Marios.
Available in Robot 2015.
If you find your post answered press the Accept as Solution button please. This will help other users to find solutions much faster. Thank you.
Hello,
I need to verify the concrete cone failure for a connection. I tried to do so manually, folowing the Concrete Design Guide 1992-4-2:2009 chapter 6.2.5 which has the same equation as Robot presents (CEB 9.2.4). However, I couldn't get the same result for the parameter Ac,N0 and Ac,N, as you can see below:
But Robot got this one:
Since scr,N=480mm and Ac,N0=scr,N*scr,N shouldn't AcN,0 be egual to 2304 cm^2 and not 8190cm^2 as Robot presents?
Is there any reason for this difference? Is there any other updated document I should be following?