Ab min for top reinforcement
EY23
Message 1 of 14
EY23
Hi all,
I'm surprised that I didn't found any post regarding this issue,
can someone give me some explanation about the hight Abmin for top reinforcement for Rc beam.
I am using RSA 2015 SP5 with ACI 318M-11. I modeled the slab as material orthotorhy in order to try to simulate One way-joist slab.
the beam dimesion is 70x30 cm.
Replies (13)
Message 2 of 14
Artur.Kosakowski
Autodesk Support
Autodesk Support
ACI 10.9.1
When N (axial force) > 0.1 * Ac * fcd
Asmin = 1%*Ac
Artur Kosakowski
Message 3 of 14
EY23
Dear Arthur,
I very appreciate your quick reply.
-can you please clarify your above statment since ACI 318-11 section 10.9.1 is the below.
-Second, it is not resnable to get a hight axial load since it a Small span with only DL and LL forresidential buildings. Can this be caused by other factors?
Message 4 of 14
Artur.Kosakowski
Autodesk Support
Autodesk Support
I'm sorry but I'm not sure what I shall calrify Smiley Sad
Ast > 0.01Ag = 1%*Ag
For the value of the axial force in the beam - it is as calculated for a model of the structure you created. If you consider it as being excessive you should check why this happens and possible modify your model before running the design of the RC Beam.
Artur Kosakowski
Message 5 of 14
EY23
0.01x70x30=21 cm2
robot gives me 17.58  cm2.
and this code is for compression members.
can this huge axial load is due to wind load?(although its not significant?)
Message 6 of 14
Artur.Kosakowski
Autodesk Support
Autodesk Support
Could you attach the model please?
Artur Kosakowski
Message 7 of 14
EY23
kindly note that I tried to remove the SW underneath the beam and change the conection type between column and beam but I Still got the same issue Smiley Sad
Message 8 of 14
EY23
Please disregard the first model,
there was a roof slab plane issue that i fixed,
please note the attached one
Message 9 of 14
Artur.Kosakowski
Autodesk Support
Autodesk Support
Having your model (thank you for atatching it ) it was possible to determine what drives Amin for thsi beam. You should look at ACI 10.6.4 provisions.
Artur Kosakowski
Message 10 of 14
EY23
Thank you for your reply,
thought,clause 10.6.4 does not verify the results showing.
Is there any case that we still have the issue raised in the thread blow ?
https://forums.autodesk.com/t5/robot-structural-analysis/abmin-how-rsa-calculte-this-value/td-p/4475...
Message 11 of 14
Artur.Kosakowski
Autodesk Support
Autodesk Support
From the thread you refered to:
Thanks for solve this in the last service pack for RSA 2015. Smiley Happy
RSA 2015 SP5
Artur Kosakowski
Message 12 of 14
EY23
I had the same issue and when I updated my version to SP5 it was solved for bottom steel reinforcement,
is there any chance that the issue it is still existed for this case of top reinforcement and We didn't notice it since we rarely face it (i.e. a beam linearly on top of a wall).
it doesn't make sence to have this huge area of of top reinforcement for a beam supported linearly on top of a rc wall.
please bear with me,
kindly find attached simplified model that shows what I mean about Ab min for top steel, can u clarify why robot gives me this results?
Message 13 of 14
Artur.Kosakowski
Autodesk Support
Autodesk Support
I assume you mean the peek of the Amin visible on the diagram. It is due to applying Amin provisions of ACI for elements under pure tension (it is in the location where bending moment is zero and tension force exists). If you consider the axial force as small enough to be neglected just exclude it from the analysis and run reinforcement design for pure bending.
Artur Kosakowski
Message 14 of 14
EY23
Dear artur ,can you just clarify for me where accordin to what provision of ACI 318 robot consider this value of As min?