Linked File not lining up

2 REPLIES 2
Reply
Message 1 of 3
advandes
308 Views, 2 Replies

Linked File not lining up

Can someone explain this? From withing the piping model I link the architectural. I layout the pipe based on the fixtures, walls etc...Perfect! Now when I open the architectural file and link the piping, the piping is not lining up....It's off by like 50' +/-..????
AAG
Advance Design
2 REPLIES 2
Message 2 of 3
asommer
in reply to: advandes

When you get to the link dialog, Check the "positioning" settings at the bottom and make sure you use the same settings for both. The widely accepted setting is "auto - origin to origin.
Message 3 of 3
advandes
in reply to: advandes

Thank you!