Kyle/ Jason,
This is an old thread but the comment about the intended use for system flow config. connectors made me wonder if there is any guidence on best practice or intended use for connectors in the mechanical, electrical & public health systems.
I havent found any and now knowing when system flow configeration could be use will be very useful as Systems are now becoming more & more important. Most examples seem to be on mechanical pipework, with little on drainage & vent systems
Thanks,
Chris Powell
@KyleB_Autodesk , those links you posted work, but it appears that the videos are no longer available. Is this a personal issue, or are other people able to access this resource? Thanks in advance!
and @KMAeng the links you posted are now dead. Do you happen to have those resources still, or does anyone know of an equivalent resource/document?
Edit: Dead link request.
@Iev60047 That link that I posted to the Getting into the Flow document should help you to understand connectors.
Here it is again.
https://thebuildingcoder.typepad.com/files/me204-3_connectors_in_revit_mep_content.pdf
Preset would usually be for terminal devices such as air terminals, radiators etc. You would preset the flow value at the terminal either by typing it into a parameter or as the result of a formula.
Calculated would usually be used for source equipment such as boilers, chillers, etc. The totalised flow from all connected terminals would be calculated and passed into the equipment. Calculated can also be used for in-line equipment such as pumps, fans, balancing valves/dampers etc.
System is used in the same way as Calculated but when there are parallel pieces of equipment which each share a proportion of the total flow. When System is chosen a flow factor parameter appears and this is used to allocate flow proportion to each device e.g. two boilers in parallel would each have a flow factor of 0.5.
For equipment such as a water heater you might used Calculated on the hot supply connector then pass that value, via parameters, to a Preset connector on the cold water connection which will then in turn pass this value to a Calculated connector at the cold water tank.