I'm using Autodesk Revit MEP 2011 and can't connect a single phase Distribution Panel (DB) to a three phase DB, what must I do to be able to do this?
Also how can I circuit a 230V receptacle to a three phase DB?
Urgent help will be appreciated
Thank you
Gunther
Solved! Go to Solution.
Solved by julianjameson8403. Go to Solution.
You have to make sure you have the correct distribution system setup in the project (415/230V) and also the correct correct distribution system assigned to the panels and the receptacles.
When creating the distribution systems, you have to make sure that the voltage values match for the single phase and the individual phases of the 3 phase system.
Main Panel would have a 415/230V three phase assinged to it, the single phase pnael would have a 230V single phase distribution system and the receptacle would still be 230V single phase distribution system.
Thank you, this helped me ALOT! Thanks
My other mistake was that I used 3 wires and not 4.