Hello All,
I am having an issue with x ref not updating.
We often have jobs that repeat. So we take an acadE project and copy it over. After changing each drawing property the reflect the need project number and updating the wire numbers and components, the xref will not update.
I right click the component, select retag/update and the x ref will not update it stays the same as the previous project. When I use the surf feature it reflect the new project location so I know that the component is sourcing correctly.
Any ideas as to how to correct this issue???
Thanks
Dennis
Solved! Go to Solution.
Solved by Icemanau. Go to Solution.
It's a different command to make the xrefs update, not the retag one...
Look under components for the cross reference tab, and on that tab there will be a cross reference command..
Select the project operation, and the schematics you need to have updated and it will do the job for you.
Regards Brad
Brad Coleman, Electrical Draftsman
Did you find this post helpful? Feel free to Like this post.
Did your question get successfully answered? Then click on the ACCEPT SOLUTION button.
Hi Dennis & Brad
I have the same problems as Dennis and Brads solutions are usually correct.
However, I find that when I copy drawings from one project to another I loose the reference points.
The drawings always come in on the UCS origin but I need to set the reference.
click on drawing in the project manager, properties, drawing properties, drawing format, setup, pick set the top left margin.
I need to do this on all drawings. Am I doing something wrong? Is there a workaround?
Cheers john q
I use IEC tag mode and this is a situation when relation between parent and child is lost:
1) Parent is on the DRAWING1 and it's child is on the DRAWING2.
2) At the beginning, LOC code (or INST; I don't know about PROJ because I don't use it) for parent and both drawings are the same:
Parent LOC=AAA
DRAWING1 LOC=AAA
DRAWING2 LOC=AAA
Child LOC=AAA
This means that LOC attributes on parent and child are empty because they are the same as LOC of the drawing they are on.
3) Now, e.g. DRAWING2 LOC is changed to BBB. Because child LOC attribute is empty, ACAD Electrical uses DRAWING2 LOC as LOC code for child.
This means that now:
Parent LOC=AAA
DRAWING1 LOC=AAA
DRAWING2 LOC=BBB
Child LOC=BBB
This means that parent and child are not the same anymore, and relation is lost.
Regards,
Vladimir