The way AcadE's wire number Source/Destination arrows work is that the
"destination" end's wire number assignment is totally controlled by the wire
number on the "source" end. This means a couple things: 1) since a single
AcadE wire (network) can't have two different wire number assignments, then
AcadE must limit the number of "destination" arrows that can be inserted on
a single wire network to just one... because of the chance that two
destinations might come from two sources that control different wire
numbers, 2) a single AcadE wire (network) can have MANY different "source"
arrows tied to it going to many other "destination" arrows, all with
different "Signal" codes... but all pointing to the common source's wire
number assignment.
So, you can do what you want but you have to put the multiple "sources" on
the wires tied to your terminal, not multiple "destinations" on the wires
tied to your terminal.
wrote in message news:5221621@discussion.autodesk.com...
Is there any way to have multiple incoming wire sources go to a single
terminal? The incoming sources will have the same wire number but different
signal codes.