I have had issues building circuit that included terminal and terminal strip,
MY circuit has 8 terminals that all or located on TS1 .Four or positive and four or negative. They or located in the panel but in the circuit I have then going from terminal block in the panel to field block in the field ,that terminal in the field is smart but there is no catalog or strip id or part number because I don’t know what the device term are in the field. When I inset my circuit my terminal strip should show only all the TS1 but, it shows TS1 with 4 term .MY other four will show up in quantity with the others that don’t have catalog info.
Place a LOCation BOX around all the devices and terminals that are in the field. Assign them different LOC and INSt attributes and the when you do your reports exclude those INST and LOCS in the setup.
Regards Brad