If you use the Modify Symbol Library tool and scale an entire IEC library folder by .03937 the IEC symbols, including wire numbers, should fit nicely on an English size 34X22" border. To scale the JIC library to fit an IEC border scale by 25.4. Copy the folder of the library you want to scale and rename to something else. Like copy JIC125 and rename the copy to JICmetric or something.
The wire numbers are blocks from the library just the same as a coil or contact. By scaling the entire library folder and pointing the project properties to this scaled folder, you will cover all the bases.
There is no conversion for Form-c since JIC has no form-c contact symbol. For JIC I insert a NO and NC contact next to one another and connect the commons with a line on a layer named Jumper. This layer will pass wire number information but the wire will not appear on the wire list.
You will find that the IEC library folder has more symbols than the JIC because there are more symbols in the IEC standard.