Cable shield on MULTIWIRE

Hi,

 

is it possible to insert cable marker with cable shield on a multiwire (fan-in/out case). It need to be also reported correctly in wiring report. See the attached image. The shield connection in this case is connected both ends.

 

Mako

1 REPLY 1
Message 2 of 2
johnq
in reply to: mako68

Hi Mako  and others

 

I looked at your drawing

 

The short answer is YES.

 

I draw a wire or line depending on if I need a wire number on the shield.

 

Draw from the device and up through the shield symbol.  Then clip it back to the position you have drawn.  I have not been able to snap to the quadrent of the half circle in the symbol.

 

I question your use of using the shield as an earth cable.  You should NEVER earth both ends of a shield cable as this will cause circulating currents.  Nor shall it be used as a 0 Volt conductor in any rx232/422 etc system.

 

It is customary to earth the end at the sacrificial device unless noted by the device manufacturer. 

 

Cheers  John Q

 

 

 