is it possible to insert cable marker with cable shield on a multiwire (fan-in/out case). It need to be also reported correctly in wiring report. See the attached image. The shield connection in this case is connected both ends.
Mako
Hi Mako and others
I looked at your drawing
The short answer is YES.
I draw a wire or line depending on if I need a wire number on the shield.
Draw from the device and up through the shield symbol. Then clip it back to the position you have drawn. I have not been able to snap to the quadrent of the half circle in the symbol.
I question your use of using the shield as an earth cable. You should NEVER earth both ends of a shield cable as this will cause circulating currents. Nor shall it be used as a 0 Volt conductor in any rx232/422 etc system.
It is customary to earth the end at the sacrificial device unless noted by the device manufacturer.
Cheers John Q