I believe your block name is the problem. ACADE keys off the block name. Rename your block to V_N1_SSR1 and all should work. I have similar SSR's. I design to IEC standards. The N is the proper designator for an SSR within the IEC. If you prefer the tag to be SSR that's fine. The important thing to know about naming blocks is that the first character needs to be "H", indicating wires coming in horizontally, or "V" for wires coming in vertically. If you have a symbol with wires connecting both vertically and horizontally, use "H". The next two characters indicate the family of the component. You must use only two letters. For example "SS" for selector switch, "CR" for control relay. You cannot use 3 letters for the family type. Since the IEC normally uses single character tags (i.e. "S" for switch, "Q" for circuit breaker, "G" for power supply) insert an underscore "_" as a placeholder in the 3rd position of the name. The last position of the block name should be "1" for parent/stand-alone or "2" for a child. For example a relay coil is a parent and a relay contact is a child. Use "1"for components that have no children.