10-04-2012 04:24 AM
According to the results I am not expecting to be seeing the "Unsatisfactory Load Capacity of the Column" message. Any reason why it could still be appearing?
Please use plain text.
Product Support
Artur.Kosakowski
Re: Unsatisfactory Load Capacity of the Column
10-04-2012 04:51 AM in reply to: stroxy
Could you attach the file with this column please?
Artur Kosakowski
Product Support
Artur.Kosakowski
10-05-2012 01:09 AM in reply to: Artur.Kosakowski
Large bi-directional shear for seismic combinations.
If you find your post answered press the Accept as Solution button please. This will help other users to find solutions much faster. Thank you.
Artur Kosakowski
stroxy
10-05-2012 03:40 AM in reply to: Artur.Kosakowski
Error message still remains after manual modification of rebar to correct safety factor. See my earlier attachment.
Product Support
Artur.Kosakowski
10-05-2012 03:47 AM in reply to: stroxy
I'm not sure if I understand you correctly. What have you modified: spcaing of the stirrups? The best seems to be the increase of a cross section of the column itself.
Artur Kosakowski
stroxy
10-05-2012 04:27 AM in reply to: Artur.Kosakowski
Increased stirrup diameter in some cases and yes reduced stirrup spacing in others.  Your suggestion on increasing column dimension is however well noted ... but unfortunately  sometimes Architectural constraints determine how much column dimensions can be increased (the ever continuing saga between engineers and architects :manlol:)
Also, Sometimes when one increases column dimensions, then huge plastic moments capacity develops in the column thus making it more difficult to satisfy capacity design requirement in shear.
In  any case, I should expect the  error message to disappear once the safety ratios for the governing case is greater than 1 ... correct?
Product Support
Artur.Kosakowski
10-05-2012 06:56 AM in reply to: stroxy
Yes, the error should no longer be displayed  when all (for each of defined seismic combinations) safety ratios for shear are above 1.
Artur Kosakowski