Discussion Groups
Robot Structural Analysis
Valued Mentor
tony.ridley
Accepted Solution
Seismic Vs Spectral
979 Views, 13 Replies
03-07-2012 03:10 AM
Rafal/Artur,
It seems to me the difference between seismic and spectral analysis in Robot is that;
In SEISMIC analysis;
  • Based on the chosen code, seismic analysis works out the response spectrum etc automatically based on the input parameters (region etc).
  • The user can set an expected base shear that Robot will limit seismic base shear to.
  • Eccentricity option is available within the seismic options (can leave eccentricity zero in the preceeding modal case)
But using SPECTRAL method;
  • I need to define the correct response spectrum;
  • I need to apply any eccentricity in the preceeding modal analysis;
  • I need to do an initial run, then go back and do a second iteration to apply scaling factors to limit my base shear to the expected value.
Please confirm if my assumptions are correct, feel free to make corrections!
Tony
Please use plain text.
Product Support
Artur.Kosakowski
Re: Seismic Vs Spectral
03-07-2012 04:48 AM in reply to: tony.ridley
tony.ridley wrote:
Rafal/Artur,
Correct.
For selected codes it is possible. For the ones this option is not available you can 'scale' it defining a load combination with the appropriate load factor.
Is available in both modal analysis (accurate solution) and seismic case (simplified approach). It is the either / or choice.
Correct
Correct
Correct
If you find your post answered press the Accept as Solution button please. This will help other users to find solutions much faster. Thank you.
Artur Kosakowski
Active Contributor
03-07-2012 06:03 AM in reply to: Artur.Kosakowski
i' ve noticed that in spectral analysis the results are influenced by the the damping ratio (controled in the modal analysis menu).
How is this possible?
Product Support
Artur.Kosakowski
03-07-2012 07:26 AM in reply to: MARIOS75
Intended for situation when you have two spectra with e.g. 1% and 5 % damping and you want to average them. Then what you type in the modal analysis e.g. 3% influences the way these spectra are averaged.
Artur Kosakowski
Active Contributor
03-08-2012 07:42 AM in reply to: Artur.Kosakowski
Thank you Artur,
 5% damping will have no influence on the spectrum, is that right?
Product Support
Artur.Kosakowski
03-08-2012 07:44 AM in reply to: MARIOS75
According to my knowledge if you do not average spectra the value of damping should be irrelevant.
Artur Kosakowski
Active Contributor
03-08-2012 07:59 AM in reply to: Artur.Kosakowski
i have no averaged spectrum, just a single custom spectrum defined from a text file.
Damping (the one controled by the modal analysis menu) seems  to influence the results in an inverse maner, high damping values give high response values.
This behaviour is more clear in systems with many degrees of freedom.
Product Support
Artur.Kosakowski
03-08-2012 08:03 AM in reply to: MARIOS75
In such case I need to have a closer look at this situation. Could you send me the rtd file and indicate the differences in results you noticed as well as the corresponding values of damping you set in the parameters of the modal case please?
Artur Kosakowski
Active Contributor
03-08-2012 08:13 AM in reply to: Artur.Kosakowski
Here it is.
You can try some values of damping (e.g 1%, 50%) in the modal analysis menu and check the the columns Fx reaction.
Product Support
Artur.Kosakowski
03-09-2012 05:50 AM in reply to: MARIOS75
As far as I can see the results for single modes and SRSS combinations are the same. The difference is for CQC combinations but this is justified as damping is included in the formula.
http://docs.autodesk.com/RSA/2012/ENU/filesROBOT/GUID-9A9795B9-E2B1-4F70-BC47-FF61A312699-621.htm
Artur Kosakowski