Please can someone help?
I have two members that are loaded similarly and one fails and the other does not, can someone tell me within the results attached why one is failing?
Many Thanks.
STEEL DESIGN
CODE:
BS-EN 1993-1:2005/NA:2008/AC:2009, Eurocode 3: Design of steel structures.
ANALYSIS TYPE:
Member Verification
CODE GROUP:
MEMBER:
63 Beam_63POINT: 1COORDINATE: x = 0.75 L = 5.715 m
LOADS:
Governing Load Case:
17 1.2DL + 1.2LL + 1.2WL(S) (1+2+3+4+5+14)*1
MATERIAL:
S355 ( S355 ) fy = 355 MPa
SECTION PARAMETERS: CHS 114.3x5
h=114.300 mm gM0=1 gM1=1
b=114.300 mm Ay=1094.986 mm2 Az=1094.986 mm2 Ax=1720.000 mm2
tw=5.000 mm Iy=2570000.000 mm4 Iz=2570000.000 mm4 Ix=5140000.000 mm4
tf=5.000 mm Wply=59774.117 mm3 Wplz=59774.117 mm3
INTERNAL FORCES AND CAPACITIES:
N,Ed = -334.30 kN My,Ed = 12 kN*m Mz,Ed = -2 kN*m Vy,Ed = -1.31 kN
Nt,Rd = 610.60 kN My,pl,Rd = 21 kN*m Mz,pl,Rd = 21 kN*m Vy,T,Rd = 136.02 kN
My,c,Rd = 21 kN*m Mz,c,Rd = 21 kN*m Vz,Ed = -5.76 kN
My,N,Rd = 14 kN*m Mz,N,Rd = 14 kN*m Vz,T,Rd = 136.02 kN
Tt,Ed = 7 kN*m
Class of section = 1
LATERAL BUCKLING PARAMETERS:
About Y axis: About Z axis:
VERIFICATION FORMULAS:
Section strength check:
N,Ed/Nt,Rd = 1 < 1 (6.2.3.(1))
(My,Ed/My,N,Rd)^ 2 + (Mz,Ed/Mz,N,Rd)^2 = 1 < 1 (6.2.9.1.(6))
Vy,Ed/Vy,T,Rd = 0 < 1 (6.2.6-7)
Vz,Ed/Vz,T,Rd = 0 < 1 (6.2.6-7)
Tau,ty,Ed/(fy/(sqrt(3)*gM0)) = 0 < 1 (6.2.6)
Tau,tz,Ed/(fy/(sqrt(3)*gM0)) = 0 < 1 (6.2.6)
Section OK !!!
STEEL DESIGN
CODE:
ANALYSIS TYPE:
Member Verification
CODE GROUP:
MEMBER:
64 Beam_64POINT: 1COORDINATE: x = 0.75 L = 5.715 m
LOADS:
MATERIAL:
N,Ed = 308.06 kN My,Ed = 17 kN*m Mz,Ed = -0 kN*m Vy,Ed = -0.25 kN
Nc,Rd = 610.60 kN My,pl,Rd = 21 kN*m Mz,pl,Rd = 21 kN*m Vy,T,Rd = 120.07 kN
Nb,Rd = 610.60 kN My,c,Rd = 21 kN*m Mz,c,Rd = 21 kN*m Vz,Ed = -8.49 kN
My,N,Rd = 15 kN*m Mz,N,Rd = 15 kN*m Vz,T,Rd = 120.07 kN
Tt,Ed = 9 kN*m
N,Ed/Nc,Rd = 1 < 1 (6.2.4.(1))
(My,Ed/My,N,Rd)^ 2 + (Mz,Ed/Mz,N,Rd)^2 = 1 > 1 (6.2.9.1.(6))
Incorrect section !!!
Please increase the precision of displaying the results. From the info you provided I assume it is sort of 0.999 < 1 for one of the bars and 1.001> 1 for the other.
I have a question regarding a verification note.
Is it possible to have this: Tau,ty,Ed/(fy/(sqrt(3)*gM0)) = 1.41 > 1.00 (6.2.6)
All the efforts in the bar are very small.
What is the meaning of Tau,ty,Ed and what is the formula to calculate it ?
Thanks!