HI,
F area lenght is e/4, with e=min(b;2h)=min(27;2x7.80=15.60)=15.60m, so F = 15.60/4=3.90m.
RSA has taken h=4.62.
It means that I have to modelise the structure from ground to the top, instead of modelising from 1st floor to the top, to force RSA to take the good value of h?
thanks
Solved! Go to Solution.
Solved by Artur.Kosakowski. Go to Solution.
It means that I have to modelise the structure from ground to the top,
Yes.
If you model a part of the structure e.g. its top floor only Robot does not know if the part below is the same as the modeled one or the part you modeled is e.g. just the temporary small shed on the top of a sky scraper
The structure height is therefore used for determining the value of wind pressure rather than calculations of F therefore in your case you should add two dummy 'outer columns' below your structure.
If you find your post answered press the Accept as Solution button please. This will help other users to find solutions much faster. Thank you.
Other question : when RSA will be able to generate wind loads on a 3D frame?
EC1 are sufficiently detailed to get values for most common geometry.
Other question : when RSA will be able to generate wind loads on a 3D frame?
Due to Autodesk policy we can not tell you any development plans and tametible.
Sorry.