Discussion Groups
Robot Structural Analysis
Member
Column base plate with Eurocode: web in tension
474 Views, 3 Replies
09-13-2012 08:17 AM
Dear Sirs,
I am calculating some base plates for steel square hollow section columns. I attach a calculation file. For the worst combination the limiting condition is "column web in tension". I have tried to check the paragraph of TENSILE RESISTANCE OF A COLUMN WEB but it is impossible to me to know the geometrical parameters used by Robot to calculate the b eff = Effective width of the web for tension, as the reference formula from EN 1993-1-8, 6.2.6.3(2) and the related figures (6.6) are intended for beam to column connections. Is it possible to know how Robot transform this checking to a base plate checking?
On the other hand, regarding shear check, i have a shear key (wedge). There is a check named BEARING PRESSURE OF THE WEDGE ONTO CONCRETE. There is no cheching of the steel wedge in shear. What happens if the wedge shear resistance is lower than the concrete pressure?
Thank you for your attention.
Please use plain text.
Member
Re: Column base plate with Eurocode: web in tension
09-19-2012 07:19 AM in reply to: Gateau.Basque
¿Nobody has verified that beam-column joint checking for base plates?
Spoiler
Product Support
09-19-2012 07:24 AM in reply to: Gateau.Basque
To give you detail answer the developer has to check the program code.
Unfortunately he is on holidays. I will update this thread when I have any info.
Rafal Gaweda
Product Support
09-28-2012 02:25 AM in reply to: Rafal.Gaweda
Column web control:
There is indeed a problem of interpretation.
Control is carried out for load capacity of the column web as for concentrated load (6.2.6.3), and we should set as the capacity of the beam web in accordance with 6.2.6.8.
• The problem has already been registered for correction
Wedge control:
Shear load capacity is a component of many capacities (anchor bolts (shear, pressure for concrete, break away the edge (I do not know if it is correct engineering term)) + capacity associated with  friction + web capacity)
Since the EC3 standard does not give how to calculate the wedge we used the forulas and rules of the PN (which is complementary to most of the EC3).
PN rules require verification of load wedge pressure only in the context of concrete.
This is due probably to the fact that normally shear (cut) capacity of the wedge is incomparably greater than the compression capacity of the concrete.
Of course, in theory, a situation in which the wedge will break sooner than will be the destruction of the concrete around it is possible.
But in practice, the wedge is usually a massive ellemnt so probably the PN does not take into account the possibility of his cut.
Rafal Gaweda
