In Revit MEP 2011 I can put multiple connector elements on a receptacle. I can then connect the receptacle to two different branch panels to create a diversified circuit. The receptacle(s) will show up on both panel schedules.
When I tag the receptacle only the first panel name and circuit number show up in the tag, is there a way to have a tag show both panels and circuit numbers?
This is an issue that I had also with light fixtures with two ballasts on different circuits. As far as I have been told, researched, and experimented, secondary connectors cannot be tagged. You would have to employ Shared Parameters to accomplish this task, which requires manual inputs.
I actually found an alternative solution from a forum that I subscribe to.
Re: Tagging Diversified Receptacles
In Response To: JWilson18
Actually you can tag multiple connectors in a receptacle with the Panel Name & Circuit Number information. My 2 Gang Duplex Split-Switched Receptacle has 4 connectors and I was able to tag every connector with the circuiting info needed. How? By creating a short wire (three clicks) from each connector and by tagging these wires. See attached image. Isn't it wonderful? Wires are the only Revit objects that I know of that can pick up the circuiting information from each connector inside the same family instance. You have to be careful though when you move this receptacle because you need to select all tags and wires with your receptacle for everything to follow up.
Hope this helps,
Aldo.
Another work-around solution to something that should be basic and simple, but it works. Being careful about moving the devices will be a pain, but manageable. Thanks a ton for posting that information.