Inconsistent wire sizing

2 REPLIES 2
Reply
Message 1 of 3
auto99
496 Views, 2 Replies

Inconsistent wire sizing

when I click the wire and then properties, this is what it shows. The wire size should be #12 and not #6.  Where does Revit gets #6?  I cannot change it either, it is grey.

 

Also, why I cannot change the number of grounds and neutral to 0?  I can change the Hot Conductors, but neutral and ground always come back to 1 even if I change them to 0. 

 

 

 

 

11-26-2012 4-55-41 PM.jpg

2 REPLIES 2
Message 2 of 3
pteague
in reply to: auto99

I have had the same problem.  Revit doesn't seem to calculate the wire size correctly at all.

Message 3 of 3
MikeDabbas
in reply to: pteague

this because of voltage drop, the circuit is probably long, if you go to your wiring settings, you will notice that Max Voltage Drop for Branch circuit is 2%, if you circuit is long, Revit will do the math for you and upgrade the wire to achieve this voltage drop value...