Modeling HEPA Filters in CFDesign using Head Capacity Curve
- Highlight
- Email to a Friend
When trying to replicate the flow through a section of HEPA filter, since I don't know the permiability constant I am using the Head Capacity Curve function. I have pressure drop (in H20) versus Air Velocity (ft/min) and have converted the velocity to flow rate based on the area of the filter section my flow volume is through.
However, the pressure drop that results is approximately double what was input in the Head Capacity Curve. Any ideas as to why this happens?
Re: Modeling HEPA Filters in CFDesign using Head Capacity Curve
- Highlight
- Email to a Friend
What values did you put into the hea capactiy curve (HCC)? Screenshot might help here.
Did you try adding more mesh?
2D Resistances parts can also provide more accurate results at times.
Are you testing the setup in a smaller model that isn't NDA that you are willing to share?
Royce
- Highlight
- Email to a Friend
I have attached the setup I used, and the values I loaded for the HCC. I haven't tried to add more mesh yet.
One weird thing did occur, when I initally solved the results were approximately 0.17in H20, and some of the variables in the convergence plot had not seemed to quite level off. When I ran additonal interations the pressure drop jumped from 0.17 in H20 to 0.59 in H20.
- Highlight
- Email to a Friend
The *.cfdst file isn't a very useful file to upload, create a support share file (file menu_save share file) and upload that instead.
See this table for more information on CFD file types:
http://www.cfdesign.com/OnlineHelp/2011/User%20Int
Thanks!
Royce
- Highlight
- Email to a Friend
See attached for support share file.
I refined the mesh and re ran, and it had very similar results as mentioned previously.
- Highlight
- Email to a Friend
The poor performance is associated with a character used in the material name that is not supported. Try changing the name of the resistance to "2 inch HEPA Filter Resistance". After I removed the " character the pressure drop was more inline with expectations.
I already tested future builds and warnings are given when this character is used.
-Royce
- Highlight
- Email to a Friend
Thank you solved my issue.
Can you expect a similar issue when using any punctuation? for just the "?
- Highlight
- Email to a Friend
Here is a warning screen with the list of characters to stay away from.
-Royce
- Highlight
- Email to a Friend
Is there a standard Head Capacity Curve for HEPA filters? Where can that information be found?