    "Too small distance between reinforcement layers" when distance seems fine?

    297 Views, 8 Replies
    10-03-2012 03:18 AM

    Morning All,

     

    I'm trying to allocate 150mm deep RC slabs for very small cantilever spans. Whenever I go 150mm or  below I get the warning / error (not sure which as it doesn't say) of:

     

    "Too small distance between reinforcement layers, for panel ** it is 14.7% of it's section. The incoherence error may occur".

     

    The slabs are 150mm thick with 30mm cover. 150mm thick is overkill for such a low loaded and low span panel. Screenshot of the panel (highlighted red) attached. On analysis the "required reinforcement" comes out as 2 layers of A252 mesh T&B for this 150mm slab (screenshot for this also attached), therefore distance between T&B reinforcement is much > 14.7% of the section... Is the message a false warning?

     

    Thanks,

    Scott

    Please use plain text.
    Product Support
    Artur.Kosakowski
    Posts: 2,773
    Registered: ‎12-17-2010

    Re: "Too small distance between reinforcement layers" when distance se

    10-03-2012 03:29 AM in reply to: Opel5

    Could you make the screen capture of the last tab (reinforcement) of the reinforcement parameters assigned to the discussed panel please?



    Artur Kosakowski
    Support Specialist
    Product Support
    Autodesk, Inc.

    Please use plain text.
    Valued Contributor
    Posts: 78
    Registered: ‎08-02-2012

    Re: "Too small distance between reinforcement layers" when distance se

    10-03-2012 03:43 AM in reply to: Artur.Kosakowski

    Hi Artur,

    See attached.

    Thanks

    Please use plain text.
    Product Support
    Artur.Kosakowski
    Posts: 2,773
    Registered: ‎12-17-2010

    Re: "Too small distance between reinforcement layers" when distance se

    10-03-2012 03:48 AM in reply to: Opel5

    Actually I need this one :smileyhappy:

     

    reinf paramaters.PNG

     

     



    Artur Kosakowski
    Support Specialist
    Product Support
    Autodesk, Inc.

    Please use plain text.
    Valued Contributor
    Posts: 78
    Registered: ‎08-02-2012

    Re: "Too small distance between reinforcement layers" when distance se

    10-03-2012 03:52 AM in reply to: Artur.Kosakowski

    oops sorry, see attached :smileyhappy:

    Please use plain text.
    Product Support
    Artur.Kosakowski
    Posts: 2,773
    Registered: ‎12-17-2010

    Re: "Too small distance between reinforcement layers" when distance se

    10-03-2012 04:07 AM in reply to: Opel5

    Apparently you created the label for a different reinforcement database than you have currently declared in the job preferences which results in values of selected bar diameters not being visible. In general the discussed value is calculated as:

     

    ( panel thickness - d1 - d1' - d2 - d2' - c1 - c2) / panel thickness



    Artur Kosakowski
    Support Specialist
    Product Support
    Autodesk, Inc.

    Please use plain text.
    Valued Contributor
    Posts: 78
    Registered: ‎08-02-2012

    Re: "Too small distance between reinforcement layers" when distance se

    10-03-2012 04:19 AM in reply to: Artur.Kosakowski

    Hi Artur,

    I've checked job preferences but can't see anywhere where a custom reinforcement allocation has been selected. Materials are still general concrete there. The purpose of the "30mmcover28day" reinforcement property was to control cover and also the shuttering time in case the contractor wanted to remove shuttering at say 7 days later on.

     

    Is there a way to switch off this warning / error message that keeps popping up then if it's a false positive?

    Many Thanks,

    Scott

    Please use plain text.
    Product Support
    Artur.Kosakowski
    Posts: 2,773
    Registered: ‎12-17-2010

    Re: "Too small distance between reinforcement layers" when distance se

    10-03-2012 04:34 AM in reply to: Opel5

    Scott,

     

    The message is more informative as the calculations are performed in the same way as if the clear distance was larger. You may try to define a new reinforcement label selecting 8 mm bar diameter as used for the wire fabric type you mentioned and run reinforcement calculations again. My assumption is that the diameter you selected for the label you defined was bigger.



    Artur Kosakowski
    Support Specialist
    Product Support
    Autodesk, Inc.

    Please use plain text.
    Valued Contributor
    Posts: 78
    Registered: ‎08-02-2012

    Re: "Too small distance between reinforcement layers" when distance se

    10-03-2012 04:51 AM in reply to: Artur.Kosakowski

    Hi Artur,

    I've swapped the floor slab back to the default "RC Shell" reinforcement property which stops the false warning from popping up.

     

    Regarding the "28day30mmcover" reinforcement property, I left the reinforcement section in that property blank as the property is being used for slabs of widely ranging thickness, span and reinforcement density in the building. It was mostly to control the shutter removal / loading time.

     

    Thanks for the speedy responses :smileyhappy: Good to know it's not an issue.

    Scott

     