Unsatisfactory Load Capacity of the Column

Unsatisfactory Load Capacity of the Column

stroxy
Advocate Advocate
4,507 Views
6 Replies
Message 1 of 7

Unsatisfactory Load Capacity of the Column

stroxy
Advocate
Advocate

According to the results I am not expecting to be seeing the "Unsatisfactory Load Capacity of the Column" message. Any reason why it could still be appearing?

Accepted solutions (1)
4,508 Views
6 Replies
Replies (6)
Message 2 of 7

Artur.Kosakowski
Autodesk Support
Autodesk Support

Could you attach the file with this column please?



Artur Kosakowski
Message 3 of 7

Artur.Kosakowski
Autodesk Support
Autodesk Support

Large bi-directional shear for seismic combinations.

 

shear1.PNG

 

If you find your post answered press the Accept as Solution button please. This will help other users to find solutions much faster. Thank you.



Artur Kosakowski
Message 4 of 7

stroxy
Advocate
Advocate

Error message still remains after manual modification of rebar to correct safety factor. See my earlier attachment.  

  

0 Likes
Message 5 of 7

Artur.Kosakowski
Autodesk Support
Autodesk Support

I'm not sure if I understand you correctly. What have you modified: spcaing of the stirrups? The best seems to be the increase of a cross section of the column itself.



Artur Kosakowski
0 Likes
Message 6 of 7

stroxy
Advocate
Advocate

Increased stirrup diameter in some cases and yes reduced stirrup spacing in others.  Your suggestion on increasing column dimension is however well noted ... but unfortunately  sometimes Architectural constraints determine how much column dimensions can be increased (the ever continuing saga between engineers and architects Man LOL)

 

Also, Sometimes when one increases column dimensions, then huge plastic moments capacity develops in the column thus making it more difficult to satisfy capacity design requirement in shear.

 

In  any case, I should expect the  error message to disappear once the safety ratios for the governing case is greater than 1 ... correct?

0 Likes
Message 7 of 7

Artur.Kosakowski
Autodesk Support
Autodesk Support
Accepted solution

Yes, the error should no longer be displayed  when all (for each of defined seismic combinations) safety ratios for shear are above 1.



Artur Kosakowski