    Wire Size Label bug

    218 Views, 2 Replies
    11-05-2012 10:58 AM

    I seem to have discovered a bug with the wire size label.  If I edit the wire type so that a neutral is not required, the label stops showing the ground conductor size as well.  I can see it in the properties window, it shows the 3 hot sizes and the ground size, it just will not show up in the view.  Anyone have a suggestion to fix this, or seen this before?

    Please use plain text.
    New Member
    Posts: 2
    Registered: ‎09-12-2012

    Re: Wire Size Label bug

    11-05-2012 11:12 AM in reply to: bbrovont

    I just discovered that the wire size parameter in the power system properties shows the correct number of conductors, but the wire size parameter for the actual wire geometry only shows the hot conductors, if there is no neutral.  Hopefully someone else has seen this before, and has a solution.

    Please use plain text.
    Product Support
    Chris.Aquino
    Posts: 288
    Registered: ‎06-27-2010

    Re: Wire Size Label bug

    11-21-2012 11:58 AM in reply to: bbrovont

    I would make sure that "Share Neutral Conductor" and "Share Ground Conductor" are both unchecked for the wire type. The tag and Properties Palette should now show the correct number of conductors.