    Re: multi level terminals

    03-19-2008 09:06 AM in reply to: driesterer
    If you are using a terminal symbol that keeps the same wire number on both
    sides, and you have a wire connected to both sides, the wire number will be
    the same. Be sure you are not choosing a schematic terminal symbol that has
    a 99 and 100 next to it. This type of terminal forces a wire number change
    across it. In TSE if you see two wires on one side of a terminal and none
    on the other, you can move one to the other side using the toggle wire
    destination tool at the bottom of the TSE. The only time there should be a
    wire number on either side of a terminal is if there is indeed a wire
    connected to that side.

    wrote in message news:5880022@discussion.autodesk.com...
    Hi Doug,
    Quick question on terminals. When I select and insert a terminal, how do I
    get it to keep the same wire # on both sides of the term?
    Regards,

    Doug McAlexander
    Electrical CAD Industry Specialist
    Independent Consultant/Instructor/Mentor
    AutoCAD Electrical, VIA/WD, Toolbox/WD, ecscad, promis-e, RSWire

    Web site: www.ECADConsultant.com
    E-mail: ECADConsultant@gmail.com
    Phone: (770) 841-8009
    Please use plain text.
    Contributor
    Posts: 11
    Registered: ‎06-14-2006

    Re: multi level terminals

    03-19-2008 09:26 AM in reply to: driesterer
    I am using the terminal with the wire number above it. When I insert it on top of an existing wire that has a wire number, it adds a new wire number to the down stream side of the new terminal. When I have a term at the end of a wire and add wire to connect to a component, it does not carry the wire number across the terminal.
    Please use plain text.
    *Expert Elite*
    Posts: 2,528
    Registered: ‎10-18-2003

    Re: multi level terminals

    03-20-2008 08:31 AM in reply to: driesterer
    I cannot be sure what is going on without seeing the drawing. In the
    meantime, double-click one of your terminal symbols and check the block
    name. It should be HT0W01, HT0W02, HT0W03, HT0W04, or HT0W05. Also check
    your project properties to be sure you don't have the box checked to force a
    new wire number for each wire in a network. This box should not be checked.
    See attached.


    wrote in message news:5880311@discussion.autodesk.com...
    I am using the terminal with the wire number above it. When I insert it on
    top of an existing wire that has a wire number, it adds a new wire number to
    the down stream side of the new terminal. When I have a term at the end of a
    wire and add wire to connect to a component, it does not carry the wire
    number across the terminal.
    Regards,

    Doug McAlexander
    Electrical CAD Industry Specialist
    Independent Consultant/Instructor/Mentor
    AutoCAD Electrical, VIA/WD, Toolbox/WD, ecscad, promis-e, RSWire

    Web site: www.ECADConsultant.com
    E-mail: ECADConsultant@gmail.com
    Phone: (770) 841-8009
    Please use plain text.
    Contributor
    Posts: 11
    Registered: ‎06-14-2006

    Re: multi level terminals

    03-20-2008 08:52 AM in reply to: driesterer
    You nailed it. In the Project Properties, under Wire Numbers, ON PER WIRE BASIS was checked. I unchecked it and the numbers stay the same on both sides of the terminals. I cannot wait for the book.
    Dennis
    Please use plain text.
    *Expert Elite*
    Posts: 2,528
    Registered: ‎10-18-2003

    Re: multi level terminals

    03-20-2008 08:58 AM in reply to: driesterer
    Glad to help Dennis.

    wrote in message news:5881371@discussion.autodesk.com...
    You nailed it. In the Project Properties, under Wire Numbers, ON PER WIRE
    BASIS was checked. I unchecked it and the numbers stay the same on both
    sides of the terminals. I cannot wait for the book.
    Dennis
    Regards,

    Doug McAlexander
    Electrical CAD Industry Specialist
    Independent Consultant/Instructor/Mentor
    AutoCAD Electrical, VIA/WD, Toolbox/WD, ecscad, promis-e, RSWire

    Web site: www.ECADConsultant.com
    E-mail: ECADConsultant@gmail.com
    Phone: (770) 841-8009
    Please use plain text.
    Distinguished Contributor
    Posts: 173
    Registered: ‎03-03-2006

    Re: multi level terminals

    01-18-2013 08:14 AM in reply to: dougmcalexander

    doug,

    i've been working through your suggestions in this post, i'm using what looks like the same 4point terminal in the example picture where all 4 connections are jumpered internally, so i edited the terminal to be 4 levels with 1 wire connection point on each level (I then copied that block property to every terminal on the list, so they're all the same). I've been associating terminals and keeping each to a max of 4 connections on my own (even though it allows 8) Some terminals are showing up as highlighted yellow and i cannot find anywhere what that means...

     

    In short terms, I have schematics where the common power wires may have wires connected via DOTs on a ladder bus, and the same wire # used on single terminals for devices elsewhere in the schematics. I don't care which levels the wires are connected to or which terminals are sharing which wires, i just want a total count for how many termination points i have for each given wire number and be able to set up the terminal block layout based on that requirement.

    any thoughts?

     

    Please use plain text.
    Distinguished Contributor
    Posts: 173
    Registered: ‎03-03-2006

    Re: multi level terminals

    01-18-2013 09:00 AM in reply to: iomaxx

    one other question as well, when i have it working correctly, i then have the correct layout with the exact number of terminals i want, but i'm not sure how to get that list of terminals on the layout exported to a CSV file. When i run a schematic report, it shows every listing of each terminal, without taking into account the association i've done in the TSE...