AutoCAD Electrical
Reply
Topic Options
- Subscribe to RSS Feed
- Mark Topic as New
- Mark Topic as Read
- Float this Topic to the Top
- Bookmark
- Subscribe
- Printer Friendly Page
Separate contacts
Options
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Highlight
- Email to a Friend
- Report Inappropriate Content
137 Views, 1 Replies
06-04-2012 12:09 PM
Anyone know a way to separate the cross reference contact cross reference locations on a parent coil. I have safety relays that carry NO, NC and NO timed NC timed contacts and would like for those types of contacts to be separated on the parent cross reference not just NO/NC. I have tried table type cross reference format but cant seem to get the type field to display anything but NO/NC
Re: Separate contacts
Options
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Highlight
- Email to a Friend
- Report Inappropriate Content
10-11-2012 05:08 AM in reply to:
breierg
You can always use another pin type (type 4) for the timed NO/NC's. Some work involved, but it will work as expected, especially with table cross-references.
THL
Please select "Accept As Solution" if this post answers your question. Kudos don't hurt either. ;-)

