    Separate contacts

    137 Views, 1 Replies
    06-04-2012 12:09 PM

    Anyone know a way to separate the cross reference contact cross reference locations on a parent coil. I have safety relays that carry NO, NC and NO timed NC timed contacts and would like for those types of contacts to be separated on the parent cross reference not just NO/NC. I have tried table type cross reference format but cant seem to get the type field to display anything but NO/NC

    Please use plain text.
    Distinguished Mentor
    rhesusminus
    Posts: 569
    Registered: ‎09-21-2007

    Re: Separate contacts

    10-11-2012 05:08 AM in reply to: breierg

    You can always use another pin type (type 4) for the timed NO/NC's. Some work involved, but it will work as expected, especially with table cross-references.

     


    THL
    Please select "Accept As Solution" if this post answers your question. Kudos don't hurt either. ;-)