Issue with parent child Relatioshi p
Options
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Highlight
- Email to a Friend
- Report Inappropriate Content
46 Views, 1 Replies
04-29-2004 12:38 PM
When we have 2 or more like parent devices such as a control relay coil that
are named the same thing but have different locations being fired from PLC
Outputs in a seperate Panel and then do a component cross reference update
all the relays think they are related.
Example:
PLC Outputs (Rack in MCP1) firing coils to 3 relays called CR1 (each living
in a seperate panel lets say CS1, CS2, and CS3 are the panel names)...(in
this scenario, we are simply providing an outputs to turn on devices
controlled by others...interlocks in other words) when we do a component
cross ref update the three relays (all named the same but have different LOC
values) think they are related...one of the 3 gets a cross ref that points
to the other two...
Shouldn't the fact that 3 parent devices (in this case HCR1) that live in
different panels not reference each other? If I am doing something just
totally off the wall here please tell me what it is. Basically in any OEM
equipment that is out there, the device names are typically the same and if
you are controlling many of them there would be times that the only
differentiation would be its LOC attribute value.
I also posted this on the Beta Feedback page...sice this issue affects both
versions
*Nate Holt \(Autodesk\)
Re: Issue with parent child Relatioshi p
Options
- Mark as New
- Bookmark
- Subscribe
- Subscribe to RSS Feed
- Highlight
- Email to a Friend
- Report Inappropriate Content
04-29-2004 01:05 PM in reply to:
*Wayne Gatlin
Wayne,
This is a situation where you probably should turn on AcadE's "Combined
Installation/Locatioin and component Tag mode (IEC-style)" option for your
project. AcadE will include the INST and LOC values you assign (or the
drawing config's default "IEC setup" LOC/INST values) in determining unique
parent tag names. Sor, if you have a relay CR1 in location "PNL1" and
another relay CR1 in "PNL2", they're treated correctly as individual devices
and all of the child cross-referencing is kept separate. You turn this mode
on via the Project > Misc Settings dialog (first toggle) and it's done on a
per-project basis.
Let me know if it appears that I'm not understanding the question or issue
here.
thanks!
Nate.
"Wayne Gatlin" wrote in message
news:40915a5e$1_1@newsprd01...
> When we have 2 or more like parent devices such as a control relay coil
that
> are named the same thing but have different locations being fired from PLC
> Outputs in a seperate Panel and then do a component cross reference update
> all the relays think they are related.
>
> Example:
> PLC Outputs (Rack in MCP1) firing coils to 3 relays called CR1 (each
living
> in a seperate panel lets say CS1, CS2, and CS3 are the panel names)...(in
> this scenario, we are simply providing an outputs to turn on devices
> controlled by others...interlocks in other words) when we do a component
> cross ref update the three relays (all named the same but have different
LOC
> values) think they are related...one of the 3 gets a cross ref that points
> to the other two...
>
> Shouldn't the fact that 3 parent devices (in this case HCR1) that live in
> different panels not reference each other? If I am doing something just
> totally off the wall here please tell me what it is. Basically in any OEM
> equipment that is out there, the device names are typically the same and
if
> you are controlling many of them there would be times that the only
> differentiation would be its LOC attribute value.
>
> I also posted this on the Beta Feedback page...sice this issue affects
both
> versions
>
>