Hi Alejandro,
The values are related and ultimately tie back to the ladder's insertion
coordinate. Let's say that you have it set up to insert vertical ladder
columns. The left-hand vertical bus of the ladder starts at X coordinate of
25.0 and the ladder width is 100 units (meaning that the right-hand vertical
bus wire has an X coordinate value of 125.0.
"Output module offset from hot bus" = 10.0 means that an output module is
going to insert into the first ladder at X-coordinate of 35.0 (25.0 + 10.0)
"Input module offset from neutral" = 10.0 means that an input module is
going to insert into the first ladder at X-coordinate 115.0 (25.0 + 100.0 -
10.0)
Let's say you set up to have two ladders per drawing and ladder to ladder
distance is 150 units. That means that the second ladder will pop in at
X-coordinate 175.0 (25.0 + 150.0). Output module into the 2nd ladder will go
in at X-coordinate 185.0 (175.0 + 10.0) and input module at 265.0 (175.0 +
100.0 - 10.0).
Does this explanation answer your question or am I totally missing it?
Nate.
wrote in message news:5017697@discussion.autodesk.com...
Hi Nate, sorry for the late reply.
No, itĀ“s not what iĀ“m seeing. I write offset 10 and get 20 for example. For
me it works like they were relative offsets. I have an input module, and if
i use the both offsets (input and output modules) it works kind of like a
slider. Maybe itĀ“s in the way I defined the modules? We use ZWorld PLCs and
they didnĀ“t come with the libraries.
Thanks.