Hi,
As you could see in the picture I have a wire 2508 which is a 24VDC connected to a distribution block.
Usualy we don't draw distribution block in the scheme.
But in the table of terminals I find that X20 37 is connected to 33CS1 , X20 34, X20 28, X20 22 etc.
This is true because I didn't draw the distribution block, but this is the usual way.
I woul like in the table of terminals find only a row for X20 37 because only two wire is connected to X20 37 terminal.
Any Idea.
Thanks
Max
Go to the schematic and clear the wire sequence. Then set it to how you require it.
ACADE has set the sequence to be DIRECT-TO-TERMINAL for some of the wires. Once that is cleared and you set the sequence you want, run a full Project Rebuild including wire connections.
Then regenerate your terminal table to check.
Regards Brad
Brad Coleman, Electrical Draftsman