Hi All,
I inserted a 3 phase power supply in my drawing today ,hpw1_3ph, from the jic125 folder. The attribute code is set to PW but my tag which is set up as
%S%N%F always displays a G for the %F location.
What's up with that?
Thanks,
Bob
Solved! Go to Solution.
Solved by dougmcalexander. Go to Solution.
If you make a new .txt- file in your project folder and name it wd_fam.dat
Then type e.g.:
G,PS
...and save the file. Close and restart autoCAD if it is open.
The next PS you now inserts will be tagged PS instead og G.
Class designation letter "G" is for the IEC standard. If you are using stock power supply symbols from Autodesk, this can happen. They simply copied the power supply symbols from the IEC library folder and pasted them into the JIC folders. I don't know why they did this but you have multiple options:
The power supply symbols in the NFPA library folder are correct. The NFPA library began shipping with release 2013. You must select it during installation. If you did not, you can go to Windows Control Panel>Programs and Features and perform a feature update on AutoCAD Electrical. This will take you back to the standards selection portion of the installation dialogs and you will be able to select additional libraries you might not have selected previously.
After you install the NFPA library you could copy the power supply symbols from that folder to your JIC125 folder. Just bear in mind that the JIC symbols are outdated anyway. Note: There are 4 files for the power supplies, two horizontal and two vertical, 1-phase and 3-phase. Their file names are:
hpw1_1ph.dwg
hpw1_3ph.dwg
vpw1_1ph.dwg
vpw1_3ph.dwg
Another option is to edit the symbols directly and change the TAG1 default value from G to PW. Make backups first. Note: The power supplies in the JIC folders appear to have been scaled versions of the ones from the IEC folder and thus the wire spacing is not optimal for a typical ladder diagram, and the location of the + and - attributes is quite a distance from the graphical portion of the symbol. You are still better off using the symbols from the NFPA library folder.
Another option is to employ a wd_fam.dat file, as explained on the Tips and Tricks page of my web site under the heading of "Understanding some of the various support files used by AutoCAD® Electrical." This optional file forces class designation (TAG) letters to be overruled by your preference, as defined in the wd_fam.dat file. But again, this only changes the class designation letter, not the appearance of the symbol, the wire spacing, or the attribute placement, thus the NFPA symbol would be a better choice.