Room Area and Occupancy
davidtetro
Message 1 of 23
davidtetro
I have been trying to find an answer to this on the discussion groups and cannot.  I was wondering how to go about doing this.  I have a building with multiple spaces in it.  I need to figure the occupancy of each space for egress and toilet fixture calculations.
I have tried toying around with formulas in the schedule by making a formula column and bringing the room area into the equation.  However, the results in the schedule are identical to the formula - the formula isn't calculating.  I tried placing an equal sign first, tried different types of characters and I cannot seem to get the formula correct.
In this example, it is a college classroom building so all the rooms have an occupancy of 1 person per 20 net square feet - so I am trying to get the room area to be divided by 20 - I cannot seem to get that calculation to work...
Any help or suggestions or ideas?
Thanks.
Replies (22)
Message 2 of 23
leothebuilder
You need to add a property definition to your sapce object.
In the Style manager, select "Documentation Object" then "Property Set Definitions" then "Space Objects"
Add an automatic property and in the dialog that appears select from the "Space" properties that are available "Base Area" and click ok.
Now add a "Formula" property.
Name this "Occupancy".
From the bottom left of the dialog box select "base area"
it should now appear in the top left area of the dialog box enclosed in brackets with a light grey background.
After (or behind) this add operator "/20".
In the top right hand pane you can see a sample result.
If all is correct close the dialogs.
This "Occupancy" can now be visible on the properties pallete when you select a space object, provided of course that the PSD has been attached to the space object.
You can now have this "Occupancy" PSD as a column in your schedule.
If you have a different occupancy requirements you can embelish the PSD by adding a manual PSD for the occupancy count and then add a formula whereby the base area is divided by the manually entered occupancy count. (all your rooms in a school will not be at 1 per 20, you may have store rooms, offices etc.)
Message 3 of 23
davidtetro
Leo - thank you - I will look into doing this!  I appreciate it!
Dave
Message 4 of 23
tevansERD
I am working on the same type of project. I set up a formula and manual definition in my SpaceStyles PSD. The formula is
[BaseArea]/[Occupant_Load]. Then I go into each space style attach the PSD and enter the divisor. The problem I have found are areas that have a divisor of 0 such as a toilet or restroom. For example if a restroom is 82 sq ft I get 82/0 in the schedule and it wont add up the total occupancy. Is there some way I can change the formula so it will behave correctly, if then statement or something? I am not too versed in VB so a little iffy on this part.
Message 5 of 23
leothebuilder
Your correct, a number divided by zero will give you an undesirable result.
Some simple VB statement to return an actual zero result would be the answer.
I don't know enough to help you with that.
I'm sure David Koch will jump in as soon as he reads this post.
Message 6 of 23
David_W_Koch
There are two problems with calculations that involve division by a value that could be zero:
1.  As previously noted, division by zero produces an undefined result, and therefore an error in VBScript.
2.  Even if you try to use a conditional statement (such as If statement) to test for a zero value and only perform the division if the value is non-zero, VBScript evaluates the entire statement, not just the parts on the logical path, so if division by zero exists, even in the section that should not be evaluated, an error condition will still occur.
Fortunately, it is possible to write a formula that works around this limitation, as can be seen in the attached sample file.  There are, no doubt, many ways to have ACA help in the calculation of occupant loads and I know others have done far more with this than is shown in the sample file here, but this should get you past the issues with division by zero in a formula property.  The file was created in ACA 2011, so anyone using ACA 2010 or later should be able to take a look at the file.
I chose to create new Property Set Definitions [PSDs] for the newly created properties, rather than add them to the out-of-the-box [OOTB] PSDs, on the theory that that would make migrating to future releases easier, by keeping my customizations separate.  You could just as easily add them to the OOTB PSDs if you want.  I also chose to make the Occupant_Load property part of a style-based PSD.  This assumes that you make use of different Space Styles for different space types/uses, and that each Space Style would always have the same occupant load factor.  This allows you to enter the occupant load factor in the Space Style once, rather than for each instance.  If you do not use different Space Styles for different space types, you could add the Occupant_Load property to an object-based Property Set Definition and enter the load factor for each Space you create.  (Choose an appropriate default value for that property if you go that route.)  The Space Styles used here are all OOTB ACA 2011 styles, with the custom SpaceStylesCalc PSD attached and a value for the Occupant_Load property entered.  Spaces that have no occupant load (non-simultaneous occupancy areas) are set to 0.
If you want to use a style-based property, but want the ability to occasionally override that value on an individual Space, that can also be done; if you cannot figure out how to do so, post back and I will try to find time to add that to the sample file.
The SpaceObjectsCalc PSD is object-based and contains the Occupants formula property.  This property uses the OOTB SpaceStyles:BaseArea property as the area on which the occupancy load calculation will take place.  The example file does not attempt to allow for the fact that, depending upon the applicable code, some occupancy load factors will be based on gross square feet and others on net square feet.  The calculation involves dividing the SpaceStyles:BaseArea property by the custom SpaceStylesCalc:Occupant_Load property value.
occLoad = [SpaceStylesCalcs:Occupant_Load]
If occLoad = 0 Then
	doCalc = 0
	occLoad = 1
Else
	doCalc = 1
If doCalc = 1 Then
	RESULT = [SpaceStyles:BaseArea] / occLoad
Else
	RESULT = 0
The formula property starts off by setting a variable called occLoad to the value of SpaceStylesCalc:Occupant_Load.  It gets around the division by zero issue by using two If statements.  The first tests the value of occLoad.  If occLoad is zero, then the variable doCalc is set to 0 and occLoad is reset to 1.  [Any non-zero value would do, since the formula property will not return a calculated value when SpaceStylesCalc:Occupant_Load is set to 0.  If occLoad contains a non-zero value, doCalc is set to 1 and the value of occLoad is not changed.
At this point, we now have a variable that tells us whether or not a calculation should take place (doCalc) and a variable for the divisor that will not be equal to zero.  The second If statement tests the value of doCalc.  If it is set to 1, then formula property returns result of dividing the value of the SpaceStyles:BaseArea property by the value in occLoad (the original value from SpaceStylesCalc:Occupant_Load).  If doCalc is set to 0, then the formula property returns a value of 0.
Notes:
1.  In the Enter Sample Values area of the formula property definition, the Format for the SpaceStyles:BaseArea property has been changed from the default Area, which rounds to two decimal places adds " SF" (imperial units version) to the area value, to a custom Property Data Format called Standard-8, which is a copy of the OOTB Standard Property Data Format with the precision increased to the maximum eight decimal places.  The text suffix of the Area Property Data Format will cause math calculations to fail.  The increase in precision is probably overkill, givent the calculation at hand.  If you have large drawings with many Spaces, you might see an improvement in performance by using the OOTB Standard Property Data Format (three decimal place precision), or a custom one with less precision.
2.  I created a custom Property Data Format called Occupants, which I applied to the formula property.  This does two things - it adds a text suffix to the result (" OCC").  If you plan to use this value for further calculations, you will want to change the applied format to one that is only numeric in the formula property definition, as was done for the SpaceStyles:BaseArea property in the SpaceObjectsCalc:Occupants formula, as indicated in "Note 1" above.  The other thing is does is round the calculated value up to the next whole number.  When doing occupant load calculations, I always round any fractional amount up to the next whole person.  If you choose to do your rounding this way, be certain to set the Round Off value to 1, as well as set the rounding to Up.  Leaving the value set to 0 can have unexpected results.  I did a series of articles on rounding in ACA properties (ADT properties at the time) back in August and September of 2005.  I have not tested rounding much since then, but expect that things probably still work the same in more recent versions.  If you are having problems with rounding using a Property Data Format, there are ways to calculate the desired rounding as part of the formula property.  Those articles from 2005 and the referenced sample files show how.
http://architects-desktop.blogspot.com/2005/08/rounding-up-property-data-values.html
http://architects-desktop.blogspot.com/2005/08/rounding-revisited.html
http://architects-desktop.blogspot.com/2005/09/rounding-redux.html
http://architects-desktop.blogspot.com/2005/09/rounding-to-death.html
3.  I added a Schedule Table into the sample file to display the pertinent property values associated with the Spaces in the sample file.
David Koch
AutoCAD Architecture and Revit User
Blog | LinkedIn
Message 7 of 23
David_W_Koch
My apologies for forgetting about the automatic emoticons.  Every place you see :O, imagine that you see a colon ":" followed by a captial "O".
David Koch
Blog | LinkedIn
Message 8 of 23
davidtetro
David - you are a genius!  However, I am a simple person and I avoid scripts.
In my project, I left out any input value for rooms that were not being scheduled for occupancies.  So, in my tables/schedules, I onitted the non-occupant rooms (the rooms with an occupant value of zero).  This way, I was able to avoid that situation entirely.
You can achieve this also by providing classifications to the rooms that are going to have an occupancy of 1 or greater - this way, the schedules will not pick up the rooms that have a zero occupant condition.
Message 9 of 23
tevansERD
David- the occupant column is not adding correctly. I don't know if this is due to rounding or some other issue. I have attached a PDF showing the issue. Also if you divide the area equally it rounds to the next higher. In this example I divided 88 by 88 which should result in 1 person but it shows 2.
Message 10 of 23
David_W_Koch
Looks like your schedule table is being cut off in the PDF you posted.  I would not have been able to do much trouble shooting in a PDF, anyway.
Are your certain that your Spaces are exactly 88 square feet, and not 88.00000001 square feet?  ACA does math on the raw values, not the formatted values.  Your Schedule Table may report an area of 88 SF, but if that is the result of applying a Property Data format that has zero decimal place precision rather than the actual value, the occupant load may round up.
As for the occupant total issue (which I cannot see as it is beyond the edge of the PDF), my previous post did allow that there might be issues with rounding.  I did not anticipate someone wanting to generate a total number of occupants by checking the total box for that column.  Once again, ACA does math on the raw, unformatted values, and if you want to have a total for the occupant load (a perfectly reasonable request, and one that I would probably want as well, on a real project), then using the Property Data Format to do the rounding is not a good idea.  You should, instead, have the formula property handle the rounding.  More than you ever wanted to know about making Schedule Table column totals reflect the sum of the actually displayed values can be found in this blog post:
http://architects-desktop.blogspot.com/2011/11/rounding-and-column-totals.html
That post also has links to the rounding articles to which my first post in this thread linked.
For the occupant load calculation, all we want is for the value to round up for any fractional amount.  This can be done in the formula quite easily.  Once way is shown below.  In the second If statement, instead of setting return values as was done in the original file, I set the "result" to a variable named occs.  A third If statement was added, testing the result of subtracting the integer portion of occs from occs.  If this is not equal to 0, then occs is reset to the integer portion of occs plus 1.  If it is equal to zero, then occs is a whole number and there is no need to reset the value.  Finally, the value in occs is returned as the RESULT.
If occLoad = 0 Then
	doCalc = 0
	occLoad = 1
Else
	doCalc = 1
If doCalc = 1 Then
	occs = [SpaceStyles:BaseArea] / occLoad
Else
	occs = 0
If occs - Int (occs) <> 0 Then
	occs = Int (occs) +1
RESULT = occs
In the attached drawing file, I modified the schedule table from the first posting to add a total to the occupant load column.  The sample file contains spaces whose areas and occupant load factors result in fractional amounts.  With the revised formula, the raw number is the same as the displayed number, and the total is the sum of the displayed numbers.
David Koch
Blog | LinkedIn
Message 11 of 23
tevansERD
Taking this one step further, is there a way to have a single row entry for multiple rooms with the area totaled for all of the same rooms. For example if there are 2 toilets to have a single row with the room name of Toilet (or whatever) and the sq Ft the total for both toilet rooms? I know you can now use grouping but the areas are on separate rows. Hope this makes since
Message 12 of 23
tevansERD
When using the grouping feature in ACA 2013, it will group room names but not the sq footages. In the attached example there are 2 stockrooms, stockroom only appears once but each square footage appears on separate lines. Is there a way to total these then divide by the divisor. The way it is now it adds an extra occupant to the occupancy load which is unnecessary since the total of the 2 stockrooms is under the 300 divisor. The cad file is too large to attach
Message 13 of 23
David_W_Koch
If both stock rooms are the exact same area (as opposed to rounding to the same area) and the values in all other columns are likewise, you can add a quantity column and the rows will collapse into one.  If you do not want to show the quantity, you can hide that column.  If you want the total area, you can add a formula column that would show the product of the quantity column and the area column.  (If you only want to show the total area, you can hide the area column, too.)
David Koch
Blog | LinkedIn
Message 14 of 23
tevansERD
It would be highly unlikely that 2 rooms would be the exact same size. As shown in the attached the areas for same room names would not add together and collapse to a single line. This would be required to get a more accurate Occupancy load.
Message 15 of 23
David_W_Koch
You may want to look into Zones.  You can assign Spaces to Zones, and the Zones have an automatic property that reports the total area of all Spaces and other Zones (if any) assigned to them.  It is likely a bit more work to set up, but short of doing some serious customization (well beyond that with which I have experience), it is the only way I know of to aggregate the areas of multiple spaces.
David Koch
Blog | LinkedIn
Message 16 of 23
I have tried this but occupancy is not visible on my proerties pallette? Can anyone help?
Message 17 of 23
leothebuilder
Make sure the "visibility" box is checked when creating PSD's.
That is in Style Manager>PSD
You can hide or show PSD's in your properties palette.
Message 18 of 23
alogan
David,
I've been using your formula for a year or so now, and it works beautifully.
My question - Is there a way to input a fixed occupancy without it trying to calculate based upon area (ie an assembly occupancy with fixed seating), and still have it function in a schedule table?
Aaron
Message 19 of 23
David_W_Koch
Sure.  You will need a property to hold the fixed property value, and then modify the formula property to use that value instead of the calculated value.
In the attached file, I added a new, manual integer property to the SpaceObjectsCalc PSD, called Occupant_Override, assuming that this should be set on a per-Space basis, rather than once for all Spaces of a particular Space Style.  I made the default value 0, and that value means that the Area/Occupant Load value should be calculated, if possible, and used as the RESULT.  The formula property gets modified as shown below, adding a test for the value in the Occupant_Override property (assigned to a variable called occOverride).  A new If test has been added.  If the value in occOverride is zero, then all of the previous formula's If statements get executed (in other words, no change in the result).  If the value in occOverride is set to anything other than 0 (presumably, positive integer values would be entered), then that value becomes the RESULT.
occOverride = [Occupant_Override]
If occOverride = 0 Then
	If occLoad = 0 Then
		doCalc = 0
		occLoad = 1
	Else
		doCalc = 1
	If doCalc = 1 Then
	Else
		occs = 0
	RESULT = occs
Else
	RESULT = occOverride
NOTE:  This formula does not check to see if a non-zero value entered into the Occupant_Override property is less than the calculated value, and if so, return the calculated value instead.  That could certainly be done, if you wanted to make certain that an occupant load less than the code-mandated minimum could not be "accidentally" entered as an override value.  The point here was to demonstrate that an override is possible.
In the attached file, I have updated the previous file to include the Occupant_Override property and amended the Occupants formula property as shown above.  I added a column to the Schedule Table to show the value of Occupant_Override for each Space.  Off 119 and Lobby 104 have override values other than zero.  I also noticed that the previous version of the Schedule Table had no sorting applied, and chose to sort this version by the SpaceObjects:Number property, in ascending order.  The file is in AutoCAD 2010 format, so anyone running ACA 2010 or later should be able to open it.
David Koch
Blog | LinkedIn
Message 20 of 23
alogan
Great!
I added "SpaceStyles:OccupantsFixed" PSD, and modifyed my "SpaceObjects:Occupants" PSD formula accordingly.
Would you know of a way to return a zero (0) result as "--" (double dash)?
Aaron
